jjones2 (Customer) asked a question.
I have 2 PLCs and 2 HMIs on 2 different (but same) machines.
I need to be able to operate both machines, from each HMI. (mainly in case of failure of an HMI).
The screens and PLC programs are a 1:1 match.
I just finished building the 1st HMI. 22 screens in total. I do not want to have to copy 22 screens, just to change all the different objects to a tag with a new device. (I think i worded that right?). Basically i will be duplicating all the tags, and importing them as "DEV002" instead of "DEV001". All PLC addresses are the exact same. What's the best way to go about this? I'd say theres roughly 300 objects that i would have to go through and change to the new tag name. Is there a faster way?
There is something you could do. Less than ideal, but it beats retagging 300+ objects.
Step 1: Save your original project
Step 2: Immediately save your project as a different name.
Step 3: Using the new project name, go to Setup> Panel Manager and change the name of the PLC device (ex. DEV001, change to DEV002). Also change the IP address to that of the new PLC (assuming your using Ethernet). Click OK to save your changes and close Panel Manager.
Step 4: Go to Tool> Screen Library
Step 5: In the Screen Library window, save each of your screens to the library by dragging them to the bottom right panel of the Screen Library window. Each time a screen is dragged to the save panel, a window opens where you can rename the screen and option to save tags. You will want to save tags. After adding all your screen to the library, close the window and save the project.
Step 6: Open the original project and go back to Tool> Screen Library.
Step 7: All of your saved screens should appear in the library (lower right panel), where you dragged them earlier. Drag them back over into the project area. After dragging the screens into your project, you should notice that all the objects on the new screens have the same tagnames but with an appended (1). As example, original tagname "LowLevel1" will be named "LowLevel1(1)" on the new screen. Each of the new tags will reference the same PLC address as the original but for a different PLC (DEV002).
Something Im unsure of is what would happen if any of your original tagnames were already at max characters. Hopefully, that isn't the case.