Hi i have a dl-205 plc, dl-260 cpu with a H2-ECOM10 comm card i need to communicate with it via another plc with modbus tcp. (dl260 will be the slave) is there something to configure on plc or ethernet card? i have done this often with click plcs but didnt do it yet with dl260 and ethernet comm. Also i forgot to say that this dl-260 is also a modbus master tahts communicate with others devices. can it be a master and a slave ?


  • adccommunitymod (AutomationDirect)

    Created Date: February 24,2015

    Created by: carmusic

    i did some test without success, i tried the peer to peer setting in the netedit3 but can't choose modbus option as you can see in picture

    http://bictm.com/images/modbus.jpg

  • adccommunitymod (AutomationDirect)

    Created Date: February 24,2015

    Created by: bcarlton

    I beliieve Modbus TCP is only available on the H2-ECOM100

  • adccommunitymod (AutomationDirect)

    Created Date: February 25,2015

    Created by: carmusic

    could a firmware update for the h2-ecom solve the problem?

  • adccommunitymod (AutomationDirect)

    Created Date: February 25,2015

    Created by: carmusic

    i also have a computer with kepware with koyo drivers connected on this plc, is there any modbus slave software that could link to kepware so i can access it via the other plc.

  • adccommunitymod (AutomationDirect)

    Created Date: February 25,2015

    Created by: bcarlton

    I don't think that there is any firmware update which will allow the ECOM to have Modbus TCP like the ECOM100.

  • adccommunitymod (AutomationDirect)

    Created Date: February 25,2015

    Created by: franji1

    could a firmware update for the h2-ecom solve the problem?

    The old ECOM module does not have many of the advanced features like in the ECOM100: Sending EMAIL, Modbus/TCP, PEERLINK, et. al. It's a completely different (limited) processor and memory (old ECOM module utilizes the old 80186). Hence, there are no feature set advances available via firmware upgrades for these old ECOM (non-100) modules.

    You will need to purchase an ECOM100 module of you want to do Modbus/TCP.

    The 260 Serial Port 2 CAN do Modbus/RTU, but you would need to have it available for connection to your Kepware PC, which would also need to utilize Modbus/RTU over serial, not Ethernet, on your PC.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: February 23,2015

    Created by: carmusic

    Hi i have a dl-205 plc, dl-260 cpu with a H2-ECOM10 comm card

    i need to communicate with it via another plc with modbus tcp. (dl260 will be the slave) is there something to configure on plc or ethernet card?

    i have done this often with click plcs but didnt do it yet with dl260 and ethernet comm.

    Also i forgot to say that this dl-260 is also a modbus master tahts communicate with others devices.

    can it be a master and a slave ?