adccommunitymod (AutomationDirect) asked a question.

dl205 ethernet network

Created Date: October 25,2007

Created By: atfab

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I have a project that will require a 205 w a 260 cpu 2 operator interfaces and 4 expantion racks and several drives I would like to put them all on a single network. is this possible or do I need different networks for the drives,IO and HMI?


  • adccommunitymod (AutomationDirect)

    Created Date: January 04,2008

    Created by: john3049

    I am currently doing something very similar. Have you looked recently in the catalog??

    It seems that the expansion racks are becoming a thing of the past and everything is going to "Flex I/O ". Automation Direct's version is their Terminator I/O. You can have 1 processor with virtually unlimited I/O points.

    The Terminator I/0 utilizes an ethernet switch (similar to a hub) to connect to the PLC with an ERM module. The one thing that is not in the catalog but in the instructions is that you want a dedicated ethernet switch for you ERM module and do not connect any other stuff other than the Terminator I/O. If you need access to a PC, use an ECOM module and another switch.

    The Operator Interfaces will connect to the switch that the ECOM module is connected to.

    Also, if the distance is greater than 300 ' between PLC's use their Ethernet Radios. I am using three for my current project.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: October 25,2007

    Created by: atfab

    I have a project that will require a 205 w a 260 cpu 2 operator interfaces and 4 expantion racks and several drives I would like to put them all on a single network. is this possible or do I need different networks for the drives,IO and HMI?