Murphy Switch

Created Date: June 24,2007

Created By: David_L

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

What am I missing? I am doing some thats seems to be simple but for the life of me I can't figure it out. The Murphy switch has a sensor reading the teeth on the starting fly wheel. In the start mode, as it rotates, I read 600-700 hz, when it starts, I get around 3850 to 3890 hz. I have the rpms set at 1800 rpms, I need to read the the low hz (0-700) to disengage the starter when running, and to read the higher hz in case the diesel would over rpm or under rpm. The problem is that I cannot seem to make the D-05 DR-D to monitor this. I have been using a function generator to sent the same type of signal to this PLC and it seems to work until 5.2 mega hertz with no problem.....Any help would be useful. Thanks


  • adccommunitymod (AutomationDirect)

    Created Date: June 24,2007

    Created by: David_L

    Last line S/B 5.2 K hertz, not mega.......sorry

  • adccommunitymod (AutomationDirect)

    Created Date: June 24,2007

    Created by: bcarlton

    Note the limitation on high speed counting in the manual.

    The available high-speed input features are:

    • High Speed Counter (5 kHz max.) with up to 24 counter presets and built-in interrupt subroutine, counts up only, with reset

  • adccommunitymod (AutomationDirect)

    Created Date: June 24,2007

    Created by: franji1

    CTRIO module supports higher frequencies. How high do you need to go?

  • adccommunitymod (AutomationDirect)

    Created Date: June 24,2007

    Created by: David_L

    The max that I need to monitor 3.9 khz, if I could do that with V memory or something fast enough to monitor it,that would be great. It is a stand alone unit and starts when the power goes out more than 10 minutes or so. DO-05 DR-D seemed like a good choice being 12-24 vdc powered.

  • adccommunitymod (AutomationDirect)

    Created Date: June 24,2007

    Created by: David_L

    What am I missing? I am doing some thats seems to be simple but for the life of me I can't figure it out. The Murphy switch has a sensor reading the teeth on the starting fly wheel. In the start mode, as it rotates, I read 600-700 hz, when it starts, I get around 3850 to 3890 hz. I have the rpms set at 1800 rpms, I need to read the the low hz (0-700) to disengage the starter when running, and to read the higher hz in case the diesel would over rpm or under rpm. The problem is that I cannot seem to make the D-05 DR-D to monitor this. I have been using a function generator to sent the same type of signal to this PLC and it seems to work until 5.2 mega hertz with no problem.....Any help would be useful. Thanks