adccommunitymod (AutomationDirect) asked a question.

DL105 dead

Created Date: August 05,2003

Created By: Rick

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

This is the second F1-130AR in a year that has died. I'm told for no apparent reason. No lights at all. It is as if it has no power. Input voltage is good, 117VAC. Any ideas or suggestions?? Has anyone had simlar problems?


  • adccommunitymod (AutomationDirect)

    Created Date: August 05,2003

    Created by: Rick

    This is the second F1-130AR in a year that has died. I'm told for no apparent reason. No lights at all. It is as if it has no power. Input voltage is good, 117VAC. Any ideas or suggestions?? Has anyone had simlar problems?

  • adccommunitymod (AutomationDirect)

    Created Date: September 01,2003

    Created by: elevmike

    You too?? No lights or action. I couldnt figure it out so I took it apart to look for a fuse, or loose connection. No such luck. It lasted for about 6 months before it went dead. This was the only falure of about 10 DL105 applications I have done.

  • adccommunitymod (AutomationDirect)

    Created Date: September 02,2003

    Created by: Rick

    This is the second out of five that has gone dead for me. I also took one apart and did find that a 10 ohm resistor that is connected in series with the incoming AC power was smoked. I replaced it but unfortunatly it smoked again...The other one that went dead did not show this resistor as being smoked...both of these were about a year old.

  • adccommunitymod (AutomationDirect)

    Created Date: September 02,2003

    Created by: FACTSTech

    If the power LED does not come on when input power is applied then the 130 power supply has failed or been damaged and the module should be returned for repair. The most likely cause of this is high voltage spikes coming in on the input power terminals.

    Is the input power fused separately from the relay load power?

    For 110/120VAC application the PLC only should be fused at 0.5 amps. The loads are to be fused accordingly to your application. DO NOT jumper the relay commons back to the INPUT power connections. Please see pages 2-10 and 2-11 in the D1-USER-M.

    Are the relays switching inductive loads? See 2-22 of the 105 User Manual for details on this.

    Is there surge suppression across the coils of the inductive loads? See 2-23 of the 105 User Manual for some surge suppressor part numbers.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: September 02,2003

    Created by: JimHoward

    The DL105 PLC's have removable terminal blocks (top and bottom). I have seen these terminal blocks crack from age and abuse, resulting in very strange problems with the DL105 PLC's. As the electrical contact "fingers " of the terminal blocks do not "grip " the printed circuit board contacts of the CPU, the "fingers " of the terminal blocks simply press against the PCB, requiring that the structural integrity of the plastic terminal blocks to make contact.

    Thus, I'd recommend you unscrew both terminal blocks and examine them closely. You can buy spares from Automation Direct.

    Jim

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: September 03,2003

    Created by: Rick

    The terminal strips were the first things I checked. Like I said earlier, the 10 ohm resistors in the incoming power was smoked. I'm checking on what FACTSTech recommended at this time. Anyone know who would repair this..assuming bad power supply is it worth the cost to repair. I still have one that I haven't creamated quite yet...

  • adccommunitymod (AutomationDirect)

    Created Date: September 03,2003

    Created by: FACTSTech

    If the module is outside the AutomationDirect warranty period (One Year from Date of Purchase), call FACTS Engineering at 800 783 3225 x121 to request an RMA for repair.

  • adccommunitymod (AutomationDirect)

    Created Date: September 08,2003

    Created by: RHanrahan

    I just have to ask though, @$149 for PLC, is is worth sending back for repairs?

  • adccommunitymod (AutomationDirect)

    Created Date: September 08,2003

    Created by: Rick

    True...