adccommunitymod (AutomationDirect) asked a question.

D05 and FAISONET

Created Date: July 24,2003

Created By: CET

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Hello Folks I have an RS 485 network using FAISONET cards, it serves 9 D05's and is running Lookout on a very fast PC. The problem is the scan rate to the PLC's, it takes about 2 minutes to scan all PLC. The stats are as follows: LOOKOUT: com driver poll rate = 100 ms LOOKOUT LINKS: baud 38400, parity=odd, data bits=1,flow=rts/cts,timeout=1000ms, data timeout=20,000ms, retries=2 PLC's PORT 2: time out=4000ms, rts on delay=100ms, rts off delay=5ms, baud=38400, stop bits=1, parity=odd. Lookout handles about 225 points including 9 charts with a single pen each. Except for the charts, the other points never change. The trend and object resolution is at .1. Can any one out there think of some way to increase the scan time from the existing 2 minutes? Thanks to all in advance CET


  • adccommunitymod (AutomationDirect)

    Created Date: July 24,2003

    Created by: CET

    Sorry......it is an RS422,4 wire network.

    NOT AN RS 485

  • adccommunitymod (AutomationDirect)

    Created Date: July 24,2003

    Created by: marksji

    Never tried Lookout with anything but ethernet, but my guess is that you 've got Lookout polling the network so often that the time for data is actually very short. Try changing your poll rate to 500ms and see if you have better overall performance.

  • adccommunitymod (AutomationDirect)

    Created Date: July 29,2003

    Created by: CET

    Good Morning and thanks for your time and reply.

    I changed the poll time to 500,1000, 5000,10000 and 18000, it still takes approx. 2 minutes to poll all the PLC's.

    I'm stumped, the slot on my D05 is taken up by an analog card so ethernet is out of the question.

    Anyone out there have any idea ?

    I again thank you in advance.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: July 29,2003

    Created by: toml

    CET, Is there also plc to plc communication involved in this system?

  • adccommunitymod (AutomationDirect)

    Created Date: July 29,2003

    Created by: CET

    Nope, the only communication is with lookout.

    No control, only data.

    Geez you guys are quick with the responses,

    cant tell you how much I appreciate it.

  • adccommunitymod (AutomationDirect)

    Created Date: July 29,2003

    Created by: franji1

    Are you getting any comm errors? Check the link status.

  • adccommunitymod (AutomationDirect)

    Created Date: July 29,2003

    Created by: CET

    No data errors, I do get errors when the data timeout is below 5,000 ms.

  • adccommunitymod (AutomationDirect)

    Created Date: July 29,2003

    Created by: marksji

    Is your network terminated correctly? If you connect an ohm meter at either end of the network does it show the proper impedance? I 've had odd issues on proprietary networks when things weren't terminated with the proper impedance before.

  • adccommunitymod (AutomationDirect)

    Created Date: July 24,2003

    Created by: CET

    Hello Folks

    I have an RS 485 network using FAISONET cards, it serves 9 D05's and is running Lookout on a very fast PC.

    The problem is the scan rate to the PLC's, it takes about 2 minutes to scan all PLC.

    The stats are as follows:

    LOOKOUT:

    com driver poll rate = 100 ms

    LOOKOUT LINKS:

    baud 38400, parity=odd, data bits=1,flow=rts/cts,timeout=1000ms, data timeout=20,000ms, retries=2

    PLC's PORT 2:

    time out=4000ms, rts on delay=100ms, rts off delay=5ms, baud=38400, stop bits=1, parity=odd.

    Lookout handles about 225 points including 9 charts with a single pen each.

    Except for the charts, the other points never change.

    The trend and object resolution is at .1.

    Can any one out there think of some way to increase the scan time from the existing 2 minutes?

    Thanks to all in advance

    CET

    Expand Post