adccommunitymod (AutomationDirect) asked a question.

DirectSOFT32 baud rate

Created Date: December 28,2002

Created By: JERRY-ALA

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Hello, Using the DS32 software I seem unable to connect to the DL05 at a speed greater than 9600 baud. This is sometimes to slow to use the DataView to monitor. Is there something I should be doing or is this the only speed to program/develope? Thanks in advance.


  • adccommunitymod (AutomationDirect)

    Created Date: December 28,2002

    Created by: JERRY-ALA

    Hello, Using the DS32 software I seem unable to connect to the DL05 at a speed greater than 9600 baud. This is sometimes to slow to use the DataView to monitor.

    Is there something I should be doing or is this the only speed to program/develope?

    Thanks in advance.

  • adccommunitymod (AutomationDirect)

    Created Date: December 29,2002

    Created by: cj

    Using port 1 (port to the left) you can only connect at 9600 baud. But if you configure port 2 (port to the right) you can connect all the way up to 38400 baud. You must configure port 2 first while connected through port 1.

    Go to the menu selection and choose PLC then SETUP and then Setup secondary comm port.

  • adccommunitymod (AutomationDirect)

    Created Date: December 29,2002

    Created by: JERRY-ALA

    Thanks CJ, I will give it a try.

    :-)