Hello, Using the DS32 software I seem unable to connect to the DL05 at a speed greater than 9600 baud. This is sometimes to slow to use the DataView to monitor. Is there something I should be doing or is this the only speed to program/develope? Thanks in advance.
Created Date: December 28,2002
Created by: JERRY-ALA
Hello, Using the DS32 software I seem unable to connect to the DL05 at a speed greater than 9600 baud. This is sometimes to slow to use the DataView to monitor.
Is there something I should be doing or is this the only speed to program/develope?
Thanks in advance.
Created Date: December 29,2002
Created by: cj
Using port 1 (port to the left) you can only connect at 9600 baud. But if you configure port 2 (port to the right) you can connect all the way up to 38400 baud. You must configure port 2 first while connected through port 1.
Go to the menu selection and choose PLC then SETUP and then Setup secondary comm port.
Created Date: December 29,2002
Created by: JERRY-ALA
Thanks CJ, I will give it a try.
:-)