adccommunitymod (AutomationDirect) asked a question.
Created Date: March 13,2000
Created By: NickZim
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
I have a problem connecting a Remote Master unit (D4-RM) to a Remote Slave (D4-RS). My setup is as follows I have base unit D4-08B-1 with A DL450 CPU then a D4-ECOM Card In The first Slot after the CPU then four D4-16NA input Cards then An Output Card D4-12TR and the another D4-16NA and finally on the Local Base a Remote Master (D4-RM).After the local base I have three Expansion bases with an assortment of Input and output cards that fill up the following expansion bases.Then I have the Remote Slave Base On the remote I/O Base. http://forum1.automationdirect.com/board/smile.gif Software loaded into PLC to Allocate The Remote Inputs X560 - X577 which is the only card on my Remote Slave Base. SP0 ----! !-----------------LD K1A LDA O7406 FILL K0 This is A New Rung SP0 ----! !-----------------LDA O40427 OUT V7404 LD K16 OUT V7405 SET 670 Before Loading This Program To The PLC The Following Lights Are Illuminated Remote Master PWR ON RUN OFF DIAG OFF PAR OFF I/O OFF LINK OFF MSTR ON Remote Slave PWR ON I/O OFF RUN OFF PAR OFF DIAG OFF LINK ON Once I Have Loaded The Program And Power Cycled The PLC I Get The Following Light Illuminating Remote Master PWR ON RUN OFF DIAG OFF PAR OFF I/O ON LINK OFF MSTR ON Remote Slave PWR ON I/O OFF RUN OFF PAR OFF DIAG OFF LINK ON Rotary Switch Setting D4-RM set to 0 and D4-RS set to 1 All DipSwitch Settings have been set to run at 38.4 Baud on Both RM & RS I Have Checked the Cabling and Believe the Cable Connection Are All Correct. Please could anyone who has used these modules shed some light on my problem? http://forum1.automationdirect.com/board/confused.gif Look forward to hearing from you out there
Created Date: March 13,2000
Created by: NickZim
I have a problem connecting a Remote Master unit (D4-RM) to a Remote Slave (D4-RS).
My setup is as follows I have base unit D4-08B-1 with A DL450 CPU then a D4-ECOM Card In The first Slot after the CPU then four D4-16NA input Cards then An Output Card D4-12TR and the another D4-16NA and finally on the Local Base a Remote Master (D4-RM).After the local base I have three Expansion bases with an assortment of Input and output cards that fill up the following expansion bases.Then I have the Remote Slave Base On the remote I/O Base. http://forum1.automationdirect.com/board/smile.gif
Software loaded into PLC to Allocate The Remote Inputs X560 - X577 which is the only card on my Remote Slave Base.
SP0
----! !-----------------LD
K1A
LDA
O7406
FILL
K0
This is A New Rung
SP0
----! !-----------------LDA
O40427
OUT
V7404
LD
K16
OUT
V7405
SET
670
Before Loading This Program To The PLC The Following Lights Are Illuminated
Remote Master
PWR ON RUN OFF
DIAG OFF PAR OFF
I/O OFF LINK OFF
MSTR ON
Remote Slave
PWR ON I/O OFF
RUN OFF PAR OFF
DIAG OFF LINK ON
Once I Have Loaded The Program And Power Cycled The PLC I Get The Following Light Illuminating
Remote Master
PWR ON RUN OFF
DIAG OFF PAR OFF
I/O ON LINK OFF
MSTR ON
Remote Slave
PWR ON I/O OFF
RUN OFF PAR OFF
DIAG OFF LINK ON
Rotary Switch Setting D4-RM set to 0 and D4-RS set to 1
All DipSwitch Settings have been set to run at 38.4 Baud on Both RM & RS
I Have Checked the Cabling and Believe the Cable Connection Are All Correct.
Please could anyone who has used these modules shed some light on my problem?
http://forum1.automationdirect.com/board/confused.gif
Look forward to hearing from you out there
Created Date: March 14,2000
Created by: NickZim
Have Managed To Solve My Problem.You have to do the input and out put allocations for the whole Slave Base and in my case where there are no outputs on the slave base you load K0 to registers V7407,which is the number of output on the slave base.
This rung should be as follows if you are only using one RM & one RS unit.This tells the CPU that you have only one Slave module connected to the Remote Master.
----! !-----------------LD
K34
LDA
O7410
FILL
K0
It works like a dream by the way.Isn't is amazing if you read the manual properly how easy things are. http://forum1.automationdirect.com/board/redface.gif http://forum1.automationdirect.com/board/cool.gif http://forum1.automationdirect.com/board/biggrin.gif
Created Date: March 20,2000
Created by: Art
And a little help from Tech Support?