adccommunitymod (AutomationDirect) asked a question.

transport protocol error’

Created Date: October 25,2013

Created By: hamster

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I have a number of direct logic 440 CPU RTU’s communicating over a large Ethernet network. I noticed when ping response times are greater than 60ms I get a ‘transport protocol error’ with DirectSoft5. With a nominal response of 6 ms, everything works fine, but greater response times give a timeout error. I couldn’t find any parameter in the DirectSoft communications configuration that would correct this. Any ideas would be appreciated.


  • adccommunitymod (AutomationDirect)

    Created Date: October 25,2013

    Created by: BobO

    On the Ethernet device page of the Link Configuration, there is an Advanced button. Your timeout there is probably set to 50ms or so. Bump that up. Note that you cannot access that button while the link is in use.

  • adccommunitymod (AutomationDirect)

    Created Date: November 30,2013

    Created by: oslinjam

    Thanks bobo this helped me out it was really informative

  • adccommunitymod (AutomationDirect)

    Created Date: October 25,2013

    Created by: hamster

    I have a number of direct logic 440 CPU RTU’s communicating over a large Ethernet network. I noticed when ping response times are greater than 60ms I get a ‘transport protocol error’ with DirectSoft5.

    With a nominal response of 6 ms, everything works fine, but greater response times give a timeout error. I couldn’t find any parameter in the DirectSoft communications configuration that would correct this. Any ideas would be appreciated.

    Expand Post