Is there a way to assign a 250 PLC address to a discrete TAG. I'm trying to assign address b5000.1 to be set when a button is pressed but I keep getting an invalid data type. I 've tried V5000.1 . Can a discrete bit of a word be entered and if so how?


  • adccommunitymod (AutomationDirect)

    Created Date: March 07,2002

    Created by: tweedy

    Is there a way to assign a 250 PLC address to a discrete TAG.

    I'm trying to assign address b5000.1 to be set when a button is pressed but I keep getting an invalid data type. I 've tried V5000.1 .

    Can a discrete bit of a word be entered and if so how?

  • adccommunitymod (AutomationDirect)

    Created Date: March 07,2002

    Created by: ericn

    Just a guess, but maybe you can move V5000 to an unused V-memory location that references individual control relays?

    See the "Control Relay Bit Map " page (page 3-49 in my manual).

    For example:

    LD V5000

    OUT V40620

    Then use C400 thru C417 in the EZ-Touch as the discrete bit in the word.

    -Eric

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: March 07,2002

    Created by: franji1

    From what I 've seen of their K-sequence driver, enter:

    V(octal address)/(bit octal offset)

    In English, that would be as follows:

    DirectSoft EZTouch

    B2000.0 V2000/0

    B2000.1 V2000/1

    B2000.2 V2000/2

    ...

    B2000.7 V2000/7

    B2000.8 V2000/10 *** OCTAL BITS!!

    B2000.9 V2000/11

    B2000.10 V2000/12

    B2000.11 V2000/13

    B2000.12 V2000/14

    B2000.13 V2000/15

    B2000.14 V2000/16

    B2000.15 V2000/17

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: March 08,2002

    Created by: tweedy

    Thanks franji. That format works. I was going to rewrite the code to use internal control relays after failing to "guess " at the format needed to enter those values in.

    Thanks a heap!