escott (Customer) asked a question.
Trying to connect to an LS-XMC-E16A plc, not having much luck. I realize that there is no specific protocol for the LS PLC's but I was trying to use the more generic Modicon profile. LS PLC returns errors when trying to establish SOCKET_TCPCONNECT. If anyone has anything that might help I'm all ears. If not I'll have to hunt down a LS HMI :(
"The C-more panel is the master when communicating with this device. "
master = client
I realize you have decided to move forward with an LS panel but wanted to add some info in case others, looking further details, may happen upon this thread.
When used with a Cmore, the PLC will be the server and the Cmore will be the client.
Here is a link detailing setup for the Modbus server in the XEM CPU
Set up the Modbus Server Mode on XEM CPU
A key piece of information here is the Server Mode must be changed from "XGT server" to "Modbus Server"
Here is a link to a video demonstrating Modbus server configuration.
https://youtu.be/GaC1pulM4-k?si=8eDgPXwMtib2VRSD