buckohboy (Customer) asked a question.

I have a click master, one click slave and i am wanting to add a productivity 412 plc as a second slave the two clicks where already functioning as similar to the sample program automation direct has. I am having issues with the comm the second slave.

if the issue is scan time for both send receive slaves. how do i separate this?


  • ADC Community_02 (Automationdirect.com)

    What issue are you experiencing with the P1-412? Can you provide specifics? Screenshots of your Click rungs and TagDB of the P1-412? Or projects to each CPU?

  • buckohboy (Customer)

    updated the clicks firmware and to 4.0 i have the click sending 11 to the m412. assigned 11 to my start mod in productivity. tried offset to 10 in click produced error 2. still a no

    • ADC Community_02 (Automationdirect.com)

      Have you tried using Modbus Poll (or similar) instead of the P1-412 and are you seeing data? Sorry but haven't had a chance to look over your projects yet.

  • ADC Community_02 (Automationdirect.com)

    @buckohboy (Customer)​ I was able to get this setup and tested and all works as expected here on my end with the Click as the master to my 412 cpu as the slave device. I don't have additional slave devices connected just the 412 cpu.

     

    What exception codes or errors are you receiving?

  • ADC Community_02 (Automationdirect.com)

    I would recommend reaching out to our technical support team for additional assistance at 1-800-633-0405.