Dylan Aubrey (Customer) asked a question.

Modbus values on error

I'm using the C2-DCM to pull data from a few devices. RS485. The problem I have is if a device fails, the last pulled data stays. Is there a way to have it revert to 0?


  • PouchesInc (Customer)

    You could probably add some programming in that says if a timeout occurs or other reported error, then write a 0 to the memory address value

    • Dylan Aubrey (Customer)

      I've been toying with that, but I wasn't sure if there was something in the PLC settings that would be simple.