I am using the GS20 VVFD for a Centroid Hickory conversion on my 5hp bed mill. The parameters that have been changed are per the Centroid Tech Bulliten as follows,
Parameter Description Value
P00.02 Restore to default 10 = set parameters to 60 Hz defaults
P00.04 Drive display 7
P00.20 Frequency command source 2 = external analog input
P00.21 Operation command source 1 = external terminals
P00.22 Stop method 0 = decel ramp
P00.31 Control method 1 = external control terminals
P01.00 Maximum operation frequency 120
P01.01 Motor base frequency 60 Hz
P01.02 Motor rated voltage 230
P01.10 Output frequency upper limit 599.0
P01.12 Acceleration time 3.0
P01.13 Deceleration time 3.0
P02.04 Terminal DI4 function 5 = fault reset
P02.16 Terminal DO1 function 6 = zero speed
P3.00 Source of frequency command 1 = frequency determined by 0-10VDC on AI1
P03.20 Analog Output 3 = output current (CNC11 & CNC12 only)
P05.01 Motor full-load current 13.6
P05.03 Motor rated speed 1755
P06.01 Overvoltage Stall Prevention 0 (disable) if braking resistor is installed.
P06.44 STO Latch Selection 1 (no latch) if STO circuit is used
All other parameters are Factory.
Brake resistor is hooked to B1 and B2 with the factory jumper plate between DC+/1 and +2/B1
From manual:
" For GS20(X) drives, the external brake resistor should be connected to the B1 and B2 terminals� • If the terminals [+1], [+2], and [DC-] are not used, leave these three terminals open� • To avoid personal injury and to prevent damage to the GS20 drive; DO NOT jumper DC- to DC+, DC- to +2/B1, DC- to B2� Connect braking resistors to B1 and B2 ONLY • DC+ and DC- are connected for common DC bus, please refer to “Main Circuit Wiring Terminals” in this chapter for wiring terminal specification and wire gauge information� • Please refer to the DURApulse Drives Dynamic Braking User Manual for more information on installing brake units� (Available for free download at http://www�automationdirect�com/static/manuals/index�html�)
parameter 7.00?
Sorry for the delay.
P07.00 ~ 07.04 are the initial brake parameters.
• P07.01: DC brake current level
• P07.02: DC brake time at start-up
• P07.03: DC brake time at STOP
• P07.04: DC brake frequency at STOP
I have no clue what to set each one at. The manual gives a range for each, and I tried a variety trying to dial it in, but it is not a smooth stop. Rather violent at any speed over 900rpm, and the parms are also set for ramp to stop and the only way I can prevent VFD oud error is setting decel time to 5 seconds, then it is a long stop bordering on 10 seconds. Internal braking only, brake resistor still gets hot sitting idle /stopped/standby.
Could someone verify these AI generated settings if they will work as intended?
P00.04Drive Display Configuration7
P00.20Master Frequency Command Source2(External analog input)
P00.21Operation Command Source 11(External terminals)
P00.22Stop Method Selection0(Deceleration ramp)
P00.31Control Method Selection1(External control terminals)
P01.00Maximum Operation Frequency120.0
P01.01Motor Base Frequency60.0
P01.02Motor Rated Voltage230.0
P01.10Output Frequency Upper Limit599.0
P01.12Acceleration Time 12.6(Adjusted for 3.0s total stop)
P01.13Deceleration Time 12.6(Adjusted for 3.0s total stop)
P01.24S-curve for acceleration begin time 10.40
P01.25S-curve for acceleration arrival time 20.40
P01.26 S-curve for deceleration begin time 10.40
P01.27S-curve for deceleration arrival time 20.40
P02.04Terminal DI4 Multi-Function Input5(Fault reset)
P02.16Terminal DO1 Multi-Function Output6(Zero speed)
P03.00Source of Frequency Command1(0-10VDC on terminal AI1)
P03.20Analog Output 1 Function Selection3(Output current)
P05.01Motor Full-Load Current (FLA)13.6
P05.03Motor Rated Speed (RPM)1755
P06.01Overvoltage Stall Prevention0(Disabled to enforce brake resistor)