AIG (Customer) asked a question.
So, I have the productivity 2000 series PLC. Recently, I noticed that even without flow or pressure in the system, there were value showing on the HMI. So I felt the drift might be as a result of calibration and after calibrating the pressure transmitter, at 4mA the engineering value is still above 13107. without the PLC, using a multimeter, the measured current is steady 4mA. Same applies when the multimeter was in series with the PLC. I got 4mA on the meter but 13140 in the PLC instead of less than 13107. Please has anyone experienced this issue before?
Hi,
I have eliminated the issue to be the PLC as using a 4-20mA generator gives 4mA at 4mA. I have also used an external power supply, isolated the transmitter from the PLC and using a multimeter, its reading 4.03mA which confirms that the issue is not the PLC. I got the same value when I used an external power supply so I do not think its the control panel power supply as well. Its just strange that all the transmitters are reading above 4mA without any pressure in the system.
Thanks for your support. Its well appreciated.