kewakl (Customer) asked a question.

PAC Runtime (module) error E02204 on a P1-540.

P1-540 cannot support remote I/O. How, then does E02204 apply?

CPU was not in Run Mode.

 

SW 3.12.1.21

I do not know the firmware. If that may be important, I can retrieve it.

 

E02204

Cause:

P3-EX is not communicating with P3-550 or P3-RS. Or, local base is not communicating with its P3-550 or P3-RS. Hot swap is not enabled for the base.

--

Solution:

Verify base has power. Disconnect and reconnect base communication cable. If problem persists, replace base communication cable, or P3-EX. If problem persists, cycle power to base. If problem

persists, restart system.


  • ADC Community_02 (Automationdirect.com)

    Have you tried a newer version 4.7 of the software to see if issue persists? Thanks!

    • kewakl (Customer)

      No.

      I do not know if this error has happened before.

      This is not my project. I will approach the others.

    • kewakl (Customer)

      Interesting, PAC Suite 4.7.2.4 resolves the E02204 issue on a P3-622.

      This thread is about this same error on a P1-540 --- with NO remote I/O capability.

       

      Are the issues related? I cannot test this. Not my project.