origineng (Customer) asked a question.

Controlling Accel/Decel of Analog Out

I have an application where I have a 0-10 VDC ultrasonic sensor reading dancer height. Using a Click, I am sending a 0-10VDC speed command to a GS2.

 

It doesn't look like the Click has any built-in functionality to filter the ultrasonic analog input or accel/decel parameters for the output. Is this correct?

 

I am writing a program to control the accel/decel. This is the simplest approach I could come up with. I have no way of testing, so if anyone could give me a sanity check, that would be wonderful. Open to suggestions if there is a better way. FYI: DS11 is accel/decel factor to adjust motor response. I have it set to update every 500ms.

 

Thanks in advance!

 

image


  • bcarlton (Customer)

    As the speed command gets very close to the sensor reading the adjustment will get less and less. If this is acceptable then ok.

  • ADC_Click_PE01 (AutomationDirect)

    In the CLICK Help files there is also a filter example. Please see CL250. Hope this helps some as well