Jason Waldner (Customer) asked a question.

Productivity p1-622 modbus to powerflex 525

Has anyone ever tried to control an ab powerflex 525 using an automation direct plc. I’m talking like start and stop and different frequencies.


  • K Price (Customer)

    Yes, we have controlled an A-B Powerflex 525 using an Automation Direct PLC (BRX PLC) for stop/start and different frequencies using discrete and analog outputs, very straightforward and easy from the PLC. (The A-B guy programmed the VFD.) But I assume you are looking to control the VFD via communications.

    • kewakl (Customer)

      YAY, Rockwell still has some basic info that is not locked behind a paid contract

  • ADC Community_02 (Automationdirect.com)

    Instead of Modbus have you considered using EtherNet/IP?

  • stoic-one (Customer)

    I currently have a 2 drive setup in my shop using a BRX over EtherNet/IP.