Bar (Customer) asked a question.
Hello,
I am using a BX08-NTC module and I am using historical view to look at data recorded with it. (I am not using the "record button", just looking at the graph). I have noticed that the data is being logged to historical view every ~1.75 seconds. Is there a way to change that to have a better resolution? "Export/Logging Method" is set to 200ms. Historical Data to retain is set to 1Mb. Thanks.
My bad. I misunderstood your initial post.
The module itself does have its own internal cyclical processing. If you are using all 8 channels, I bet that slows down its processing.
Looking at the spec here
BRX Expansion Module (BX-xxNTC)
it says 2.2s is "all channel update rate @ 16.7 Hz, internal channel sampling rate).
So it appears the module is slower than the PLC scan, or even the Designer Trend View comm data update rate. Not sure how that gets processed relative to the 200ms detents you are seeing. I know temperature processing is slow.
If you require faster update rates, you might look at getting a couple of the 4 channel Universal Temperature modules BX-04UT with a "all channel update rate" of 700ms:
BX-xxUT
(the 8 channel version is 1400ms, hence why you might consider two 4 channel UT modules for the faster update rate, if required).
But if you are just trying to understand the 200ms detent on the Trend View, temperature module internal processing is just slow compared to the PLC scan. 🙂