Nrus_73 (Customer) asked a question.
A little green around the gills with Productivity PLC and am looking for some pointers please when it comes to integrating into SCADA.
Best to start with the fact that i am communicating Serially over 232 (Modbus RTU). i thought i would need a Modbus Read/Write block for this but that looks to me to be more for the PLC communicating to other devices and not to Scada as the RS232 requires a Slave node to be given in each of these blocks, however no slave node as it's talking back to the Master.
InTouch polls each of our sites approx once per minute and is only looking for status for alarming and certain timer/counters, i have these copied into 40000 registers ready to be read and written to (setpoints)
Using OIMBTCP drivers within InTouch and Modbusbridge/PLCRS.
i am sure i am missing many specific points so please ask away.
Issue found and now the P2000 is communicating with InTouch.... Nothing to do with PSuite, nothing to do with the PLC, human error..
I realized today that the Rx LED on the PLC was active but not really acting as i would expect which led me to checking the DB9 pinout again and then the ball dropped, i had not grounded the chassis of the PLC so the 5V of the DB9 had no ground reference, once grounded all good.
Boy do i feel stupid!