HamiltonWoods (Customer) asked a question.
I would like to use a Productivity 1000 or Click PLC for an OEM application. I would like to password protect the project, but I would like for the end-user to be able to change the IP Address without entering the password. Is that possible?
If this is not currently possible, can this be submitted as a feature request? I know that, in a Click PLC, SD80 and following contain a copy of the IP Address, subnet mask, etc. Could, for example, the IP Address, etc. be written to a writeable address and used to replace the configured values after a power cycle?
Or, alternatively, could the project have multiple password levels, one of which allows for changing the IP Address, etc., without revealing other aspects of the project?
@HamiltonWoods (Customer) Good news — the ability to update the CPU's IP address externally through an HMI is supported on the following Productivity CPU's:
• P1-412
• P1, P2, & P3-622
• Mini series
This can be accomplished using the Access System Parameters (ASP) instruction. For full details on implementation, please refer to help topic P327 in the documentation.