origineng (Customer) asked a question.
I am using PH50MGJ to step down 208V to 120V. The terminals that I am attaching my 208 legs (L1 & L2) have continuity. As a result, there is continuity between L1 and L2 at my two thermal protectors going to the motors. Is this OK? I always though L1, L2, and L3 should be isolated.
Per the wiring as shown in the photo, you should not have continuity between L1 and L2 on either of the motor protectors, because the wires are disconnected from the transformer's primary winding terminal screws (H1 and 208V). But when you connect those wires to the transformer's primary winding (H1 and 208V), you will get continuity between L1 and L2 on both of the motor protectors, because you have continuity from L1 to terminal block, to fuse, thru fuse to H1 screw, thru primary winding to 208V screw, to fuse, thru fuse, to terminal block, to L2. If you have continuity between L1 and L2 when the transformer primary is disconnected, then you have a problem, a wiring mistake, a short. I guess you did not yet install the 3-phase supply to the terminal blocks.