Shaneh72 (Customer) asked a question.
I have enable the OPCUA server in the setup tab.
The error light on the module will eventually start blinking slowly indicating the application is disabled.
My SD308 error is error code 1: Undefined Error
How do I clear this error?
The error light on the module will eventually start blinking slowly indicating the application is disabled.
My SD308 error is error code 1: Undefined Error
How do I clear this error?
I have enable the OPCUA server in the setup tab.
The error light on the module will eventually start blinking slowly indicating the application is disabled.
My SD308 error is error code 1: Undefined Error
How do I clear this error?
@Shaneh72 (Customer) the SD308 error codes are defined in Help Topic CL110 Error code 1 is Application disabled. This is usually caused by an issue in the the setup of the OPCUA. The most likely cause is that your time is not synced. Starting on page 32 of the C2 Applications Guide will help you set up the C2-OPCUA.
If this does not work please let me know.
Still not working.
I basically have a PLC and a C2-OPCUA card in Slot 0.
The following contain the operations I tried with the results:
1. On page 32 of the CLICK Applications guide, I was able to Adjust the PC clock to correct time and date successfully.
2. On page 32 of the CLICK Applications guide, I was able to add the SD1, DS1, and C1 addresses to the Data View successfully.
3. On page 32 of the CLICK Applications guide, I was NOPT able to add the SD1, DS1, and C1 addresses to the Node list tab.
Each time I added and entries, the entries would default back to X001 and Y001 and not save.
It appears I cannot add node to the node list which is configured as 2?
1. What is UA expert? How do I obtain that?
Please let me know.
Your help is greatly appreciated,
[cid:image001.png@01DC6E68.686EAC90]
Shane Harrington
Sr. Principal Controls & Automation,
Manufacturing Engineer
2010 E. International Speedway Blvd, Deland, FL 32724
Bldg. F
Office Phone: 386-738-8376
Cell Phone: 321-626-0287
Email: shane.harrington@cardinalhealth.com<mailto:shane.harrington@cardinalhealth.com>
UA Expert is a free OPC UA test client. It is available at HERE. It may seem a bit daunting at first but following the guide should make it easy to manage.
I am not sure what you mean by "I cannot add node to the list which is configure by 2" Do you mean array size as 2 or something else. If you can send me screen shots of you setup screen both the General and the Node List that will help me troubleshoot this with you.
Still not working.
I basically have a PLC and a C2-OPCUA card in Slot 0.
The following attachments include my configuration, node list, and UA expert page.
I add the addresses to the node list but they disappear once I close the node list tab.
I have installed UA Expert but I cannot get past the certificate page.
I will need instructions upon how to do this.
Thank you,
[cid:image001.png@01DC6E8B.E60C0850]
Shane Harrington
Sr. Principal Controls & Automation,
Manufacturing Engineer
2010 E. International Speedway Blvd, Deland, FL 32724
Bldg. F
Office Phone: 386-738-8376
Cell Phone: 321-626-0287
Email: shane.harrington@cardinalhealth.com<mailto:shane.harrington@cardinalhealth.com>
Hi,
Still not working.
I basically have a PLC and a C2-OPCUA card in Slot 0.
The following contain the operations I tried with the results:
Each time I added and entries, the entries would default back to X001 and Y001 and not save.
It appears I cannot add node to the node list which is configured as 2?
Please let me know.
Have you sync'ed the clock in the CLICK CPU to your PC? This has to be done because the OPC UA module checks time stamps and uses that clock. If the time stamps are off, it will error out.
Have you enabled the OPC UA Server in your CLICK project, downloaded that project, and switched from Stop to run mode? Network settings are applied when you switch from stop to run, so any changes you have downloaded may not be evaluated.
After you have verified that, the error LED should stop blinking.