brooksg44 (Customer) asked a question.

Setting P2CDS-622 as an ethernet/ip Adapter, When connect to this adapter with a CODESYS Control Win V3 as a Scanner I get a Program loaded - EXCEPTION. Have updated the firmware to latest version

imageAttached is the project file. bTS2_3_Adapter is the Adapter and cTS2_3_Scanner is the Scanner. Running 3.5.21.20 version of Codesys


  • FACTS_MikeSc (AutomationDirect)

    Thanks for adding the project here.

     

    That exception from my experience usually occurs on the first initial uploads of more "robust" projects.

    If you haven't already, try doing a power cycle or a reset cold which is under Online menu.

     

    In the meantime I'll take a look at the project.

     

    Expand Post
  • brooksg44 (Customer)

    Thanks for quick response. Have to do a reset cold to get adapter to run again. But as soon as I turn on the scanner exception occurs again.

  • FACTS_MikeSc (AutomationDirect)

    Hmm.. Try having the CPU switch in stop mode and do a cold reset or power cycle. Then put it into run mode after a minute or so.