brooksg44 (Customer) asked a question.
Setting P2CDS-622 as an ethernet/ip Adapter, When connect to this adapter with a CODESYS Control Win V3 as a Scanner I get a Program loaded - EXCEPTION. Have updated the firmware to latest version
Attached is the project file. bTS2_3_Adapter is the Adapter and cTS2_3_Scanner is the Scanner. Running 3.5.21.20 version of Codesys
Thanks for adding the project here.
That exception from my experience usually occurs on the first initial uploads of more "robust" projects.
If you haven't already, try doing a power cycle or a reset cold which is under Online menu.
In the meantime I'll take a look at the project.
Thanks for quick response. Have to do a reset cold to get adapter to run again. But as soon as I turn on the scanner exception occurs again.
Hmm.. Try having the CPU switch in stop mode and do a cold reset or power cycle. Then put it into run mode after a minute or so.
Quick comment- try adjusting the "ENIPScannerIOTask" priority from '1' to 3 or more so Main Task has the priority and increase the "Interval" up from 1ms to 10ms+.
Side note: "ACD" is not supported so anywhere you may have enabled, uncheck.
https://docs.codesys-p2cds622.com/en/latest/Unsupported/enip_acd.html