EugeneUng (Customer) asked a question.

PS-AMC Motion Sequencer (MSEQ), Multi-Axis Motion Sequencer (MMSEQ)

Hello,

Learning PS-AMC 4 axis here. Simply could not figure out how to use these instructions.

My setup is two servo driven linear actuators. I'm able to move them separately in position mode, but in motion sequencer nothing works. Is there an example on how to use those instructions?


  • ADC Community_02 (Automationdirect.com)

    You will need to put 'Wait for Position Move Complete' after each of the move commands like below:

    move

    Selected as Best
  • ADC Community_02 (Automationdirect.com)

    You will need to put 'Wait for Position Move Complete' after each of the move commands like below:

    move

    Selected as Best
    • EugeneUng (Customer)

      Will it work for multi axis motion sequencer? I’ll try this today and update this thread.

    • EugeneUng (Customer)

      It did work. Everything is operates perfectly.

      • kewakl (Customer)

        Thank you for asking the questions that some of us do not know needed asking. :)