Hughbshaiak (Customer) asked a question.
mostly wondering if its possible.

Hughbshaiak (Customer) asked a question.
mostly wondering if its possible.

The P2CDS-622 supports modbus communications through both Ethernet and Serial connections.
While I have not used the Proto X devices myself I would say it is very possible. If you have any other questions feel free to post.

Should be fine, if not seen:

this is in reference to the PX-EIP coupler. i am tryinig to set it up using the scanner adapter in codesys. i keep getting the error message (16#315)

What is the scanner adaptor you are trying to use or if you have a screenshot of it I can take a look at it.

Error Message 16#315 indicates that there is an invalid segment in the connection path. In order to better assist you, please provide an image of the values configured in the Connection Path Settings window of your CodeSys project, as well as an image of your PX-EIP1 configuration. I have provided my own examples below.


The prefix '16#' means base 16, which is hexadecimal, not decimal.
Therefore, the Instance ID entries should be:
Scanner to Target
Target to Scanner
Update your settings and see if you get better results.