I am trying to set-up a BRX plc to communicate with a Keyence model VS camera through the Eithernet/IP server. I am not finding any information on how to do this, and ADC support says I need to "Create a Simple Data Block" but I have had no experience using Ethernet/IP it appears to be more difficult then I expected.
Anyone here able to help?
Thank you,
Eric
That generic error is what I would expect to see with no communication at all. Incorrect IP address settings, no response from the adapter. Verify the PLC and camera are on the same subnet. There is a PING instruction in the Domore you can use to test if the camera will at least respond to a ping request from the PLC.
I believe those vision systems need to be configured and have the EtherNet/IP settings enabled before using but am not familiar with that side of it. That would be a question for Keyence.