GreenEnergy (Customer) asked a question.

Timer incorrect entry from HMI using DS bit ?

If I set value of 120 at HMI (EAS-S3ML-RN) Then it will appear as 288 at PLC (C0-00DD2-D). Seems like DS bit is only acceptable type for timers, is there any workaround for this ?


  • ADC Community_04 (AutomationDirect)

    Make sure the tag data type in the C-more project isn't set to BCD.

  • GreenEnergy (Customer)

    Yes that is what was the problem. Thanks alot !