origineng (Customer) asked a question.

GS21 Setup

I am having some difficulties configuring my drive. I need to run when powered up. I have an estop tied into the STO circuit. When the e-stop is reset, I need the drive to automatically reset and go back into a run.

 

So far, I have it running when powered up. It stops when the e-stop is hit. It resets then the e-stop is reset. But, it does not go back into run when the e-stop is reset.

 

Here is how I have it configured.

 

6.44 - 1

02.35 - 1

00.32 -1

00.21 - 1

DCM jumped to DI1

 

Any help would be greatly appreciated.

 

Thanks!

Mike

 

 

 


  • ericn (Customer)

    First off, realize that equipment shouldn't automatically restart after releasing an e-stop;

     

    Emergency Stop Device Reset: Each e-stop device, i.e. button, pull cord, foot switch, etc., is required to latch in the activated state and must be individually reset. Resetting the e-stop device is NOT permitted to re-start the machinery, only to permit restarting. (NFPA 79, CSA Z432, ISO 14118).

     

    https://machinerysafety101.com/2011/03/01/reader-question-multiple-e-stops-and-resets/

     

    That said, if you're not using the R1 relay output, wire your run signal through the relay contacts, and set P02.13 (R1 function) to 9 (Drive is Ready). When the STO resets, the relay will close with enough delay to satisfy the off-to-on requirement. There is also enough delay that you don't even need to set P02.35 to 1.

    Expand Post