lorenz0 (Customer) asked a question.
Do I need high-speed outputs to run a stepper driver with Click Plus or do relay outputs work?

lorenz0 (Customer) asked a question.
Do I need high-speed outputs to run a stepper driver with Click Plus or do relay outputs work?
You will need a DC Output module in slot 0. Take a look at the two below reference materials that will help get you going:
https://cdn.automationdirect.com/static/helpfiles/click/Click_Help.htm#292.htm?Highlight=CL292
https://www.automationdirect.com/videos/video?videoToPlay=9n1pAinn1E0&q=pto

Okay. Huge thanks! This means that a C2-14D2 module should work right? I bought the C2-14DR module but this is not a DC output module right?
This means that a C2-14D2 module should work right?
Yes
I bought the C2-14DR module but this is not a DC output module right?
Correct it is a relay module.

Thanks! Will the C0-00AC power supply work for this application or do I need the C0-01AC power supply?
If you have only 1 module then yes the C0-00AC will work. Take a look at the spec sheet below to determine if it will meet your requirements:
https://cdn.automationdirect.com/static/specs/clickpower.pdf
Another good tool is our online Click configure tool:
https://www.automationdirect.com/clickplcs/config/clickplusconfig
Copyright © 1999-2023 AutomationDirect. ALL RIGHTS RESERVED
This means that a C2-14D2 module should work right?
Yes
I bought the C2-14DR module but this is not a DC output module right?
Correct it is a relay module.