cwizard55 (Customer) asked a question.
I am having issues getting getting signals from a Prosense Pressure Sensor into my ClickPlus Analog Module.
I have a C0-01AC Power Supply, C2-01CPU, C2-08DR-6C Analog Module, and a Prosense SPT25-20-0060A.
When I use an amp meter I get a 4-20mA signal that changes with pressure applied to the pressure sensor. Atomspheric gets 4mA and when pressure is applied the mA rises. So the sensor seems to be working fine.
I want to know if I am wiring this into the C2-08DR-6C correctly. The Prosense Sensor Red wire is going to the C0-01AC power supply 24+. The Prosense Sensor Black is going to AD1I on the C2-08DR-6C Analog Module. I have wiring connecting the C2-08DR-6C Analog Module ACOM port next to the AD1I port back to the power Supply 0V(not ground).
When Config the board choosing DF1 as the AD1I register and checking the Click software system monitor I get 0.0mA despite an Amp meter hooked in serial showing 4mA. Using the same wiring config I have tried moving to AD2I, AD3I, AD4I, but get the same result.
What am I doing wrong?
It worked, Thanks for the help. I guess it needs to have a running Program. Now I need to learn Ladder logic.