lfenwick (Customer) asked a question.

I'm replacing a Panel View PV550 with a C-more CM5-T7W. I am unable to connect to my SLC5/03. I'm using cable EA-DH485-CBL for DF1 full duplex because that's what the panelview used. I get alarm PLC-001 and PLC-013. What am i doing wrong?

  • ADC_HMI_PE (AutomationDirect)

    Are you using Channel 0(DF1) or 1(DH-485) on the SLC5/03? If you are using channel 1, the CM5 does not support DH485 like the EA9 did. If you are using Channel 0, then use the EA-SLC-232-CBL.

    Selected as Best
  • ADC_HMI_PE (AutomationDirect)

    Are you using Channel 0(DF1) or 1(DH-485) on the SLC5/03? If you are using channel 1, the CM5 does not support DH485 like the EA9 did. If you are using Channel 0, then use the EA-SLC-232-CBL.

    Selected as Best
    • lfenwick (Customer)

      DH485. So when I get the new 232 cable will I have to change any settings in my slc5/03?

      • ADC_HMI_PE (AutomationDirect)

        Depends on the port settings in your SLC5/03. So long as the settings in your CM5 project and SLC Channel 0 are the same.

         

        See help file CM003 in the CM5 software.

         

        I recommend making a simple project on the CM5 with a single Numeric Entry pointing to N7:0 and make sure you get that working before trying more.

        Expand Post