JWBaker3 (Customer) asked a question.

JWBaker3 (Customer) asked a question.
Two common protocols between the two are probably
I do not know CompactLogix, but BRX PLC can be Master or Slave on either 1 or 2. How familiar are you with the two protocols on CompactLogix, as either master and/or slave? We can definitely help on the D-more/BRX side, and I'm sure there's others out there that can help with CompactLogix if you need help there.

I would recommend using EtherNet/IP Implicit Messaging (I/O Messing). Using the CompactLogix as the originating Scanner device and the BRX PLC as the target Adapter. The AutomationDirect video Team has a video that shows exactly this.
See link below.

Thanks, will it work with strings? SS0-SS10 and/or SL0 - SL10? If not I can work around that by using the string to int conversion, but would be cleaner if it will work with strings directly
Thanks again great help.
JW
Sorry, no strings. What is your data?
If it's a structure, you could create a UDT in Do-more to match exactly what is in the CompactLogix, then use MEMCOPY to copy it into/out of D or N or whatever memory. Then configure your Implicit I/O to work with the D or N or whatever memory.

I typically work with byte arrays when it comes to the device level exchange of EtherNet/IP Input Data (T->O) and Output Data (O->T). In Do-more Designer, I create Memory Blocks for Input and Output Data. I then use these in my EtherNet/IP Adapter setup. Moving raw bytes of O->T data into Strings, UDTs, and other data types is easy in Do-More Designer.
Copyright © 1999-2023 AutomationDirect. ALL RIGHTS RESERVED
I would recommend using EtherNet/IP Implicit Messaging (I/O Messing). Using the CompactLogix as the originating Scanner device and the BRX PLC as the target Adapter. The AutomationDirect video Team has a video that shows exactly this.
See link below.
https://youtu.be/qsj8899fRNs