mikeexplorer (Customer) asked a question.

Connecting a Cmore HMI to COM port 3 on Click

I plan to add a second HMI screen to an existing Click PLC. The HMI will be located some distance from the PLC so I would like to use COM port 3 (RS485) to communicate with the HMI

Can this be done and what settings would the Cmore need to communicate?

 


  • ADC Community_02 (Automationdirect.com)

    OK thanks for the details. You will use Port 1 on the CM5 for RS485. Refer to CM501 for details on setting up serial comms with a Click CPU.

    image

    Selected as Best
    • mikeexplorer (Customer)

      Port 3 is the 3 terminal RS485 port. The screen shot you posted shows it as a diferent port.

       

      • mikeexplorer (Customer)

        The Click is a C0-01AR-D I plan to use a Cmore CM5 T4W. It will be located about 50 to 75 feet away from the PLC so that is why I wanted to use the Port3 on the Click (the 3 pin RS485) Port 2 already has a EA1 3 inch monochrome HMI.

         

  • ADC Community_02 (Automationdirect.com)

    OK thanks for the details. You will use Port 1 on the CM5 for RS485. Refer to CM501 for details on setting up serial comms with a Click CPU.

    image

    Selected as Best