mikeexplorer (Customer) asked a question.
I plan to add a second HMI screen to an existing Click PLC. The HMI will be located some distance from the PLC so I would like to use COM port 3 (RS485) to communicate with the HMI
Can this be done and what settings would the Cmore need to communicate?
OK thanks for the details. You will use Port 1 on the CM5 for RS485. Refer to CM501 for details on setting up serial comms with a Click CPU.