GS4-4040, EOL1 fault.
Scalar mode.
Scalar mode.
Hi
How would u interpret this fault:
OutFreq: 1.50
OutAmp: 90.30
OutVolt: 20.0
Stuck at start up?

Slad (Customer) asked a question.
Hi
How would u interpret this fault:
OutFreq: 1.50
OutAmp: 90.30
OutVolt: 20.0
Stuck at start up?
Copyright © 1999-2023 AutomationDirect. ALL RIGHTS RESERVED
From page 6-19 of the GS4 drive manual:
https://cdn.automationdirect.com/static/manuals/gs4m/gs4umw.pdf
Hi,im more into figuring out if the drive faulted at start up, or while running.
What is the nature of the driven load? If it requires high starting torque, and your VFD is set up for a normal application, then you might be able to get it to run by adjusting the application settings of the drive. If the load is a normal one, then something is wrong with the load or the motor for it to call for 90 amps from your 60 amp drive.