Istilldontknow (Customer) asked a question.
I am using a Symax 1/2Hp or 1Hp (low amps) PMAC motor with with a GS13 or 23 drive. They are a permanent magnet design so I am putting +15Vdc to 2 of the lines (L1 & L2) and 0Vdc from the same power supply to the other line (L3) when the drive isn't running. This creates an excellent holding brake that will never mechanically wear out and provides more than enough holding torque for my application. (NOTE: I tried a 24V PS and the motor got hotter than I liked so I scaled back to 15V and it never gets over 120degrees F.)
I originally used a motor contactor with auxillary contacts to wire it through: The contactor is controlled by the drive, whenever the drive runs, it turns on the contactor sending power to the motor. When the drive is off, the 15VDC power supply sends power thru NC contacts to the motor acting as the brake.
Since I couldn't find a contactor with 3NO and 3NC contacts I used a 2NC auxillary contact block on a 3NO, 1NC contactor to get the 3NO 3NC contacts I needed to swtich between the drive and the Power Supply. I think that they did not switch mechanically fast enough on one of the 5 installations and that drive would trip intermittently on a ground fault and had to be manually reset. (NOTE: Only one out of five did this and I replaced the drive, replaced the contactor, etc. It still faulted intermittently. maybe the problem was elsewhere in the wiring but I couldn't track it down)
So, I'm looking for a cleaner solution without auxillary contact blocks and I see no reason not to use a standard 3PDT ice cube relay to switch between the drive and the power supply other than that they are only rated for 230V max. The drive is ramping the voltage up to 460V, the braking power supply is only 15VDC. Since I'm not really switching the motor with the relay at full voltage and the motors are pulling no more than 3 amps (I'm using 15A rated relay contacts) is there any REAL reason to be concerned with this arrangement?
I've already tested the ice cube relay solution with no problems whatsoever so if anyone can tell me why this would be a horrible idea I would really appreciate it. This arrangement makes a very nice brake motor replacement with nothing mechanical ever to fail or wear out. I have five units running (almost) flawlessly for over a year now.
The Ice Cube cant handle it.. You are switching from A/C to D/C then Back to A/C.. on the same contacts.. I think the Inductive Spike will kill the Contacts.. and GENERALLY they do not have enough separation between the Contact Surfaces to keep from welding.. And if they weld, you might be blowing the VFD back into the PowerSupply..
Generally you want a Reversing Contractor with a Mechanical Interlock.. So it is not Possible for both contractors to be energized at the same time.. One Contractor will have the VFD Feeding it.. One Contractor will have the 15Volt PS on it..
Contactor.. Need Two of them.. I'm using 24VAC for my Coil Switching
https://www.automationdirect.com/adc/shopping/catalog/motor_controls/iec_magnetic_contactors/iec_contactors/sc-e02p-24vac
Interlock, that Mechanically prevents both contractors from engaging at the same time..
https://www.automationdirect.com/adc/shopping/catalog/motor_controls/iec_magnetic_contactors/magnetic_contactor_accessories/sz-rm
And then 2 of the Aux Contact Tops for the Contractors.. So the Logic knows what is actually happening..
https://www.automationdirect.com/adc/shopping/catalog/motor_controls/iec_magnetic_contactors/magnetic_contactor_accessories/sz-a22t
Overbuild it rather than making it small and cute.. it will last forever..
Cap