Hughjack (Customer) asked a question.

P1 PID output issue

The productivity pid appears to give 13107-65535 output regardless of the output module. I have the combo AD/DA module which is 13 bit. I had to rescale the output from the PID before I sent it to the module to 8193 max.

 

Before I figured this out the output just stayed stuck at 66635. Is the math conversion the only way to handle this?


  • ADC Community_02 (Automationdirect.com)

    For the analog combo modules input is 13 bit and output is 12 bit resolution. I would check to see what do you have your Input Range Min/Max and our Output Range Min/Max values. These are used in calculating the scaling factor to apply to the Process Output after PID calculations.

    Selected as Best