HawkCodes (Customer) asked a question.

I am programming a P1AM-100 module with a P1AM-ETH and need help addressing 8 type-k Thermocouples.

I am programming a P1AM-100 module with a P1AM-ETH, two P1-04THMs, and a P1-08TA modules and I need help addressing 8 type-k thermocouples to send from the Arduino IDE through Modbus TCP in order to show on a EA9-T10WCL HMI. What is the correct way to send these thermocouple temperatures in Fahrenheit to the HMI continuously?


  • FACTS_MikeSc (AutomationDirect)

    On the c-more panel, you can create a Floating PT 32 tag in the tag database and assign it to a modbus input or holding register. You can use the numeric display object to display the reading on the c-more like in the example referenced above.

     

    Creating a Tag: Database --> Tag Name Database --> Add

    Note: The tag will have to be assigned to a device (p1am-100) in the device name column for the modbus address option to be available.

     

    On the P1AM-100 you can try typecasting the temp reading and write that to the modbus register:

    uint16_t whole = (uint16_t)temperature_f;

    uint16_t decimal = 100 * (temperature_f - (uint16_t) temperature_f);

     

    Hopefully that should get you going in the right direction.

     

    Expand Post
    • HawkCodes (Customer)

      The HMI is displaying that there is a PLC-001 timeout error and I followed the examples from above. I know it is not the cables because I have tested different ones and I get the same error. The serial monitor reads the temperatures correctly. So I believe the communication error is in the Arduino code or in the HMI set up. Is there a way to determine why the two will not communicate correctly?

    • FACTS_MikeSc (AutomationDirect)

      If you don't mind could you share your code?

      • HawkCodes (Customer)

        Here is the code I've been using. There are some libraries that are not used but will be implemented later once the communication error has been solved. I have also ran into the problem of not being able to read the 2nd P1-04THM module's temperatures in the serial monitor.

      • FACTS_MikeSc (AutomationDirect)

        Appreciate it. The Oven_Code_V3 on line 82 you're using a delay of 5 seconds. That's probably the issue that is interrupting communications. Try removing that and see if it works.

         

        When doing modbus with the c-more panels you'll want to avoid adding delays in your code so that the connection is always handled as fast as possible.

         

        Edit: You can use the method in the example BlinkWithoutDelay if you want to delay some piece of code or other use.

        Expand Post
  • HawkCodes (Customer)

    Taking the delay out of the code did not help the timeout error. Am I sending the values through the wrong way? and referencing them the wrong way in C-more? I am using a numeric value in order to display the temperatures.

    • FACTS_MikeSc (AutomationDirect)

      If you haven't already, I would check the ip settings and that you can ping both the p1am-100 and the c-more panel.