sailingsalt (Customer) asked a question.

Has anyone connected with EthernetIP a Click (C2-03Cpu) to a SMC (EX260-sen1).

I am trying to use AB's BootP DHCP but it won't see the EX260-sen1. I am getting no DHCP replys at all? Is the Click able to use the AB BootP? Any help would be great.

 

Larry


  • ADC Community_02 (Automationdirect.com)

    Q: Has anyone connected with EtherNet/IP a Click (C2-03Cpu) to a SMC (EX260-sen1)?

    A: The Click plc can only be an EtherNet/IP adapter (help topic CL233 & CL232). Therefore, it can't directly communicate with your SMC device.

    Selected as Best