Click Module c2-08d2-4vc wiring

I'm hooking a Trasmitter connected to a temperature sensor (Baumer Flex Top 2204-HR51) 4-20mA but I have difficulty wiring it into the c2-08d2-4vc slot module in the click. Is there a video explaining that module and how to wire it? The wiring diagram is not clear on where the wires exactlly go into the module....Thanks!


  • ADC Community_02 (Automationdirect.com)

    From the Click technical specifications:

    image

    Selected as Best
    • Acd123 (Customer)

      Thank you for your input. Do you think there is a typo in this manual that attached. Using C0-4AD2DA-1 it says inputs 0-20mA and in the config settings I edited the input range from 4-20 even though the module says 0-20mA. You think my pt500 would work if connecting it to CH1 with transmitter output 4-20mA. In the DataView i see a number but it's a bit of an offset on it needs to be calibrated and not sure which deg its showing C or F. Thanks!

      Image is not available
      pt500

      Expand Post
      • ADC Community_02 (Automationdirect.com)

        Yes your 4-20 ma output from your transmitter will work with the Click plc 0-20 ma input. Like you already did just make that adjustment in the module configuration.

         

        Believe there is configuration software that you can adjust those settings in your Baumer device. Once you know the settings you can adjust the scaling in the C0-4AD2DA-1 module configuration.

        Expand Post