I am using the click C0-04RTD card and some prosense pt100 sensors the run of cable is about 8 feet loacated in near proximity to the 480v supply wires for the VFD. The problem is once i start the drive my temp reads jump around by as much as 40 degrees. Anyone got any ideas to mitigate this?
Todd,
I had both unused channels shunted as shown. It did not help the issue.due to the complexity of running new sheilded vfd to motor wire and new sheilded m12 cords for the rtd, i tried a 4 to 20 rtd transmitter and fed my expansion card with the input and has solved the issue. The temp is stable now with motor running.