thenols (Customer) asked a question.
I have a Click Plus PLC (C2-03CPU-2), and a EB Pro compatible Maple Systems HMI (HMI5070B). I have the 3.41 FW for the PLC, and am using the EB Pro 6.08.01, the click PLC comms driver called "KOYO CLICk V3 MODBUS TCP/IP". The HMI can can communicate with the PLC, but it can only read part of the memory map. I have 2 option cards installed in the slots with the controller. the DI's on the first reside at X001-X004, and the DI's for the 2nd card are at X021-X024. But when I try and choose the addresses for the 2nd card, EB Pro says it is not available. I can only choose address from X001-X016, and then I can start again at X101, but everything in between it tells me I have an address error. Has anyone else seen this? Or do you have any ideas for me?
You know, the earlier CLICKs, only supported discrete I/O addresses of 001-016, 101-116 etc. The Plus is relatively new, Could be that the authors of Easy Builder just haven't added support yet.
For 4 addresses, I'd just copy them to C bits and let the HMI access the C bits