RC4 (Customer) asked a question.

How do you create multiple output coils on a single logic rung in the Click PLC ladder logic?

I'm trying to create a rung that, when true, overwrites the values of multiple data addresses. I can't seem to place multiple outputs on a single rung. The Line tool allows me to add a line going down to start a sub-rung, but I can't seem to take it to the right to make room for a second output coil. What am I missing?


RC4 and ADC_HMI_PE like this.
  • ADC Community_02 (Automationdirect.com)

    ****Edited*******

     If you click in the right hand column for outputs -> then hold CTRL + down arrow it will draw a line down to add another output. You can also do the same function with the line tool as long as you are in the output column.

     

    You need to have a conditional input example a normally open contact for it to compile correctly.

    image 

    Expand Post
    Selected as Best
  • ADC Community_02 (Automationdirect.com)

    ****Edited*******

     If you click in the right hand column for outputs -> then hold CTRL + down arrow it will draw a line down to add another output. You can also do the same function with the line tool as long as you are in the output column.

     

    You need to have a conditional input example a normally open contact for it to compile correctly.

    image 

    Expand Post
    Selected as Best
  • RC4 (Customer)

    Thank you. This is exactly what I needed to know.