MiSp (Customer) asked a question.
But I have no communication error..
Hi there,
Hopefully someone can help me out with a problem I have with a Click PLC C0-10DD2E-D connected to a Weintek MT8071iE HMI through ethernet (modbus).
I've setup the Click PLC ethernet port (port 1) with Modbus TCP and enabled the Modbus TCP Server (TCP Port 502).
On the Weintek HMI I've added the Koyo click V3 modbus TCP/IP device with port number 502 (UDP not selected. Also tried with UDP on, but no luck).
Both are on the same IP range with the PLC on 10.1.2.20 and the HMI on 10.1.2.10.
On the HMI I’ve created 2 buttons. One to toggle a Bit (C20) on the Click PLC and one to change a Bit on the HMI it self. When I write this to the HMI, it runs, but the button to change something on the Click PLC does not show. The button to change something on the HMI itself does show and I’ve no communication error message on the HMI.
I’m probably missing something, but can’t see what. So maybe someone can give some ideas i can try.
Many thanx in advance.
Regards,
Michiel
Took me some time, but I know what i did wrong.
In "System Parameter Settings" > "device settings" I set Location to "Remote" in stead of "Local". (I'm using Koyo click V3 modbus TCP/IP driver)
Now it works fine.
Hopefully this answer helps someone else as well.
Thanks to you all. Kind regards,