Cranford (Customer) asked a question.
I have a new spare 2711R-T10T HMI (which utilizes Connected Components Workbench) and a Click CO-10DD2E-D PLC, both can do Modbus RTU but it seems like it's the Tags in the HMI it does not recognize, I am only just beginning but put in one tag in the HMI as X001 and it gave me a warning when it compiled. Anyone had success connecting to PV800's?
thanks
Austin
You will need to assign Modbus address in your HMI that is assigned to the Click address. These can be found by going to Program -> Address Picker -> then checking "display Modbus addressing". In the HMI you would put in address 100001 for Click address X001.