I have the servo drive set up to communicate with the PLC and the PLC sees the module but when I try and push values to certain addresses through Implicit messaging I get no feedback. I generated an EDS file via the Servo software and used that to create my addresses. i am not seeing any information pulled from the servo or able to push anything as well Is there something I am missing in the configuration side of the Servo drive?
The 'Studio5kNoValues.jpg' image shows you highlighting and referencing the tag 'SureServo2:C.Address_of_P0_000x.' This is a Configuration Assembly tag which indicates the pointer ADDRESS for P0.000 (which is 0). You need to view the Input Assembly tags (T->O) that are probably labeled similar to 'SureServo2:I.Data[0]'.
On positive note, this image also indicates that you successfully connected to the SureServo2 with your1769-L38ERM and have no errors.