I'm putting together a production setup for a pressure testing and reporting rig. I have layed out the design separating AC and DC wiring. I would like to know two things...

 

  1. Is my assumption correct? DC Voltage, Cat5e data, rs232, thermocouple, analog & digital data to brx modules go into one bundle ok.
  2. AC voltage in the other

 

Also, what is the gap required? I want a tight design (shown below). I did not see any shielding I could get to help with allowing a closeby setup such as this.

 

Any other advice would be appreciated.

 

On the wire duct, blue indicates AC, grey DC

 

image


  • martinav (Customer)

    Yea I wachted that. Its a good video.

  • Todd Dice (Customer)

    There are two factors I look at when answering your question.

     

    1. Cables I've seen for DC circuits are insulated to a maximum of 300-volts. If your panel includes 480-volts AC, you want those separated.
    2. Noise from an AC circuit interfering with DC circuitry.
      • Todd Dice (Customer)