isaacbudde (Customer) asked a question.

C-More v6.73 Alarm Handling - Banner vs. List

I am currently programming an A-D EA9-T10CL for use with an Allen-Bradley CompactLogix PLC, communicating over Ethernet/IP. I am attempting to handle alarms on the HMI based on the value of various boolean tags from the PLC, which is mostly functional. I would like to have all alarms visible in an Alarm List block, which seems to work, but I would like to disable the banner display at the bottom of the screen. In other words, I would like the alarm to only display in the list, and not as an overlay over all screens available on the panel. Is this an option with the C-More series?


  • ADC_HMI_PE (AutomationDirect)

    In the Alarm Action settings, uncheck "Display"

     

    Alarm Action

    Selected as Best